Ponyboy Posted March 12, 2010 Report Share Posted March 12, 2010 Today I looked at a 1939 condominium building which was fully renovated about 5 years ago. The gas dryer is installed in the full bathroom. I can't find gas dryers specifically mentioned in my code check book. I noted it as the same safety hazard that a gas water heater or furnace would be in a bathroom. Does the code allow a gas dryer in a bathroom or not? Quote Link to comment Share on other sites More sharing options...
Mike Lamb Posted March 12, 2010 Report Share Posted March 12, 2010 You won't find anything in code or manufactuerer;s instruction not allowing dryers in bathrooms. As far as location, I would consider make-up air for combustion but that's about it. You can look at IRC SECTION G2438 (613) Quote Link to comment Share on other sites More sharing options...
Jim Katen Posted March 12, 2010 Report Share Posted March 12, 2010 Well, there's this: G2406.2 (303.3) Prohibited locations. Appliances shall not be located in sleeping rooms, bathrooms, toilet rooms, storage closets or surgical rooms, or in a space that opens only into such rooms or spaces, except where the installation complies with one of the following: blah, blah, blah. But this is a big condo building. The IRC doesn't apply to it. - Jim Katen, Oregon Quote Link to comment Share on other sites More sharing options...
Terence McCann Posted March 12, 2010 Report Share Posted March 12, 2010 Why not a bathroom I wonder? First thought that came to mind was methane build up - as a joke though. Combustion air problems? Quote Link to comment Share on other sites More sharing options...
Chad Fabry Posted March 12, 2010 Report Share Posted March 12, 2010 NY is a little different: But this is a big condo building. The IRC doesn't apply to it. 303.3 from the Fuel Gas Code applies to all buildings except residential. So, in this case, it's true for both residential and building. 101.2 Scope. The provisions of this code shall apply to the design, installation, maintenance, alteration and inspection of fuel gas piping and equipment, fuel gas-fired appliances and fuel gas-fired appliance venting systems that are permanently installed and specifically addressed herein. Exceptions: 1. Detached one-and two-family dwellings and multiple single-family dwellings (townhouses) not more than three stories in height above grade with separate means of egress and their accessory structures shall comply with the Residential Code of New York State.... ............................................................................................... 303.3 Prohibited locations. Appliances shall not be located in, or obtain combustion air from, any of the following rooms or spaces: 1. Sleeping rooms. 2. Bathrooms. 3. Toilet rooms. 4. Storage closets. 5. Surgical rooms. Exceptions: 1. Direct-vent appliances that obtain all combustion air directly from the outdoors.... 5. Appliances installed in an enclosure in which all combustion air is taken from the outdoors, in accordance with Section 304.6. Access to such enclosure shall be through a solid weather-stripped door, equipped with an approved self-closing device. Quote Link to comment Share on other sites More sharing options...
Ponyboy Posted March 12, 2010 Author Report Share Posted March 12, 2010 Why not a bathroom I wonder? First thought that came to mind was methane build up - as a joke though. Combustion air problems? Gas appliances are not allowed in bedrooms or bathrooms because of carbon monoxide poisoning and combustion air concerns. If a gas water heater is not allowed in a bathroom, shouldnââ¬â¢t a gas dryer not be allowed for the same reasons? Since it is a condominium building I figured the owners would not change the combustion air and door to the laundry room. Currently a louvered door separates the laundry room from the bathroom. I recommended installing a Carbon Monoxide detector and not using the bathtub when the clothes dryer is in operation. Quote Link to comment Share on other sites More sharing options...
Marc Posted March 12, 2010 Report Share Posted March 12, 2010 I recommended installing a Carbon Monoxide detector and not using the bathtub when the clothes dryer is in operation. You've got me there Ponyboy. 'Can't use the tub when the clothes dryer is on'? What do you think the client is going to wonder about? The tub/dryer or the inspector? Marc Quote Link to comment Share on other sites More sharing options...
Chad Fabry Posted March 12, 2010 Report Share Posted March 12, 2010 It's just a bad idea. Bath fan on blowing 150cfm out the roof and the dryer on w/ a need for combustion air and blowing 200-300 cfm through the side wall. The wind will be coming under the door at leaf blower rates. Quote Link to comment Share on other sites More sharing options...
Ponyboy Posted March 12, 2010 Author Report Share Posted March 12, 2010 I recommended installing a Carbon Monoxide detector and not using the bathtub when the clothes dryer is in operation. You've got me there Ponyboy. 'Can't use the tub when the clothes dryer is on'? What do you think the client is going to wonder about? The tub/dryer or the inspector? Marc You'r missing the heart of the question, Mark. From a safety standpoint (Carbon Monoxide poisoning), what is the difference between a gas dryer, a gas water heater or a gas furnace in the bathroom? The later two are not allowed in this location. Quote Link to comment Share on other sites More sharing options...
Jim Katen Posted March 12, 2010 Report Share Posted March 12, 2010 . . . From a safety standpoint (Carbon Monoxide poisoning), what is the difference between a gas dryer, a gas water heater or a gas furnace in the bathroom? The later two are not allowed in this location. The reference that Chad posted seems to indicate that they're all prohibited from that location. - Jim Katen, Oregon Quote Link to comment Share on other sites More sharing options...
Tom Raymond Posted March 13, 2010 Report Share Posted March 13, 2010 It's just a bad idea. Bath fan on blowing 150cfm out the roof and the dryer on w/ a need for combustion air and blowing 200-300 cfm through the side wall. The wind will be coming under the door at leaf blower rates. I've yet to see a bath fan that moves any significant amount of air. Even if they're sized correctly the ducting is so screwed up that all they do is make noise. Tom Quote Link to comment Share on other sites More sharing options...
Mike Lamb Posted March 21, 2010 Report Share Posted March 21, 2010 From yesterday. How timely. Click to Enlarge 37.3 KB G2406.2 (303.3) Prohibited locations....surgical rooms. ??? If I ever see a gas appliance in a surgical room, I'm all over it. Quote Link to comment Share on other sites More sharing options...
msteger Posted March 21, 2010 Report Share Posted March 21, 2010 I see dryers (electric and gas) in laundry areas that share space with a half bathroom often. So you are saying that the code doesn't allow laundry areas to share space with bathrooms (should a gas clothes dryer be installed)? Quote Link to comment Share on other sites More sharing options...
Jim Katen Posted March 21, 2010 Report Share Posted March 21, 2010 I see dryers (electric and gas) in laundry areas that share space with a half bathroom often. So you are saying that the code doesn't allow laundry areas to share space with bathrooms (should a gas clothes dryer be installed)? It's not a matter of what I, or anyone else, says. Here's the code section: G2406.2 (303.3) Prohibited locations. Appliances shall not be located in sleeping rooms, bathrooms, toilet rooms, storage closets or surgical rooms, or in a space that opens only into such rooms or spaces, except where the installation complies with one of the following: blah, blah, blah. Gas dryers are considered to be gas appliances. - Jim Katen, Oregon Quote Link to comment Share on other sites More sharing options...
pete moss Posted March 28, 2010 Report Share Posted March 28, 2010 . . . From a safety standpoint (Carbon Monoxide poisoning), what is the difference between a gas dryer, a gas water heater or a gas furnace in the bathroom? The later two are not allowed in this location. The reference that Chad posted seems to indicate that they're all prohibited from that location. - Jim Katen, Oregon furnaces and water heaters are unattended appliances. a gas dryer is an attended appliance there is a difference..... Quote Link to comment Share on other sites More sharing options...
Jim Katen Posted March 28, 2010 Report Share Posted March 28, 2010 . . . From a safety standpoint (Carbon Monoxide poisoning), what is the difference between a gas dryer, a gas water heater or a gas furnace in the bathroom? The later two are not allowed in this location. The reference that Chad posted seems to indicate that they're all prohibited from that location. - Jim Katen, Oregon furnaces and water heaters are unattended appliances. a gas dryer is an attended appliance there is a difference..... Where is that distinction made in the Fuel Gas Code or the IRC? - Jim Katen, Oregon Quote Link to comment Share on other sites More sharing options...
qhinspect Posted March 28, 2010 Report Share Posted March 28, 2010 furnaces and water heaters are unattended appliances.a gas dryer is an attended appliance there is a difference..... I don't like it but that's the answer. For some reason the gas dryer is considered an unattended appliance like a stove so it is allowed. So if you ever see a stove being used in a bathroom, that's OK also.[:-blindfo Quote Link to comment Share on other sites More sharing options...
Jim Katen Posted March 28, 2010 Report Share Posted March 28, 2010 furnaces and water heaters are unattended appliances.a gas dryer is an attended appliance there is a difference..... I don't like it but that's the answer. For some reason the gas dryer is considered an unattended appliance like a stove so it is allowed. So if you ever see a stove being used in a bathroom, that's OK also.[:-blindfo Oh, I understand the concept. I'm just wondering what the reference is. - Jim Katen, Oregon Quote Link to comment Share on other sites More sharing options...
Johnnyboy Posted November 15, 2019 Report Share Posted November 15, 2019 If the bathroom has only half wall with vaulted ceiling in a 1 room house is this still the same issue? Because the bed is in the same room as gas stove. Quote Link to comment Share on other sites More sharing options...